- Wisconsin
- PE (Retired) - Power Systems
The slash (/) means that both voltages are available. The cross (X) means that either voltage is available. Notice on a standard transformer the primary is often listed as 240X480 which means you can wire it for either 240V input or 480V. The transformer secondary is listed as 120/240 which means it can supply 120V and 240V at the same time.georgestolz said:Can you elaborate? I've never seen an "X" as a seperator. What does it mean?
It defines the connection of the transfomer windings. I apologize that I can't remember all of the options other than a standard 4 wire connection like 208Y/120.What is the significance of the location of the "Y"?
This is a special autotransformer connection used to effectively turn a 3 wire delta system into a 4 wire wye. This is not 100% accurate but it explains the concept.What is a zig-zag transformer?
I don't know if I am supposed to answer this one, but. I too have been miswritten electrical terms and as a result have been able to strecth many topics into mega-length discussions. One of my personal improvements goals is to be more correct in my term usage even if it is at the expense of appearing pompus at times.My apologies for offending your delicate sensibilities, I have miswritten nominal voltages in the past as well.