Good way to design an MV system?



a6z7iJj.jpg
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
I thought you were calculating...
the cable manufacturers have the capacitance of the cables listed, calculate your capacitance on each cable length to each inductor.

that’s why I’m suggesting a higher voltage class cable like a 35kV cable with the lower voltages to get the capacitance down.
that or add shunt reactors...
 

mbrooke

Batteries Included
Location
United States
Occupation
Technician
I thought you were calculating...
the cable manufacturers have the capacitance of the cables listed, calculate your capacitance on each cable length to each inductor.

that’s why I’m suggesting a higher voltage class cable like a 35kV cable with the lower voltages to get the capacitance down.
that or add shunt reactors...

I am, and leaning toward this system. However, 35kv cable energized at 33kv would be the simplest and most economical.
 