Doesn't the HH mean High Heat?Most THHN is dual rated THWN.
Sent from my LGLS990 using Tapatalk
Doesn't the HH mean High Heat?Most THHN is dual rated THWN.
Doesn't the HH mean High Heat?
Sent from my LGLS990 using Tapatalk
Thank You.Yup. Thermoplastic High Heat Nylon-coated. Rated for operating at 90*C. The W rating makes it liquid impermeable. If you look at a piece of THHN wire it will usually have both THHN and THWN on it.
I would say yes to any portion of it that houses plants.
Yes of course, bathrooms, offices, storage rooms etc.
Did anyone say it was?
Maybe we need to define green house.NEC may not consider it a wet location. But, when it looks like a giant swamp cooler, and has at least 50% humidity, and a 4 X 30 linear foot wet wall should it be qualified as a wet location?
Sent from my LGLS990 using Tapatalk
Correct, but THHN/THWN 2 is pretty common and lets you use ninety degree rating in wet locations.But the high heat provision does not apply to wet locations if the alternate listing is only THWN.