Ground bushing requirements?

herding_cats

Senior Member
Location
Kansas
Occupation
Mechanical Engineer
I'm getting ready to tie in three (3) 200A subpanels from a large 3000A MDP. My question is are grounding bushings required on both ends of the EMT or just one? I'm running 2" EMT on all three subpanels. 208vac 3-phase. If I remember right I just need bushings on the subpanel side?
 
ok awesome. I have grounding bushings on the subpanel side already I'm going to leave them. I'm in an area where inspections don't know what you guys know and don't want trouble/issues. LOL
 
ok awesome. I have grounding bushings on the subpanel side already I'm going to leave them. I'm in an area where inspections don't know what you guys know and don't want trouble/issues. LOL
Not required but also doesn’t hurt anything either , the only time you’d have to worry about additional/enhanced bonding methods when fused conductors are involved at that voltage would be in a hazardous location (250.100), or a metallic raceway/cable assembly between two non metallic boxes/enclosures
 