Re: Ground Current... Caused by motors?
Originally posted by hurk27:
Here is a quote from page 7-5 in the manual:
... "The boost converter also establishes the systems output neutral for supporting
single phase AC loads from any phase of the inverter output..."
Page 7-5 in my manual is totally different. Are you sure you have the right unit (Powerware 9330-20). I did find a section in the Service manual that refers to a Neutral Regulator on page 7-10/section 7-4. "The name Neutral Regulator indicates that this circuit may have something to do with the control or creation of the system AC neutral like what is typically seen at the output of a wye type transformer, in fact, it does not. The unit uses the neutral provided to its input from the utility feed like many loads which require a neutral. In this particular case, the term refers to maintaining a balance from the positive DC link and negative DC link to the systems neutral input.
Without the neutral regulator, various single phase non-linear loads can create an imbalance in the boost output voltage as referenced to the systems neutral. Under severe conditions, the inverter may not be able to maintain its own output and may be forced to transfer the applied load to utility bypass until the condition clears itself. With the Neutral Regulator, DC link balance is able to be maintained allowing these types of loads to be supported."
Also, in the Owner's Manual there is a drawing that shows the wiring schematic for the unit in question. It is on page A-31, titled UPS System Options Cabinet Configurations Powerware 9330 (10-20kVA) Page 2 of 8.
This drawing shows the input neutral (terminated at the Bypass connection) jumpered directly to the output neutral. The maint bypass switch used in the options cabinet does not switch the neutral, only the phases.
Hope this clears things up.