Re: Ground Current... Caused by motors?
I went into the site this past Saturday night. Oh boy, where do I start. We found 10 neutral-ground bonds in some office furniture circuits. Also, there is a generator that feeds 480 delta through a delta-wye step down transformer. The transformer then feeds through a disconnect switch. This feeds to the ATS. This is a 3-pole ATS which has the neutrals from the generator, utility and load all tied together. In the generator transformer the neutral was bonded to ground on the secondary side at XO. The disconnect switch also had a neutral-ground bond in it. With the transformer bond, in a standard application this may be normal to bond XO, but in this case because we are using a 3-pole ATS where the neutrals are all tied together, the main source neutral-ground bond will be used (at the main distribution panel). With a bond also in the generator transformer this would create a parallel path for neutral current to transfer onto the ground.
What would the code be that addresses the gnerator transformer being used as a secondary source and not a newly derived source, and therefore it should not have the N-G bond on XO.
What would the code be that addresses the N-G bond in the disconnect switch and also the bonds in the load circuits. This code would probably be the same for both. The information I have is from the 1993 code book 250.04 for the 3-pole ATS, and 250.61(B) for the other bonds. I have a 2002 code book, but am having trouble cross-referencing the codes. Any help would be tremendously appreciated.