weressl said:How will anyone KNOW without testing, if the second rod installation fulfilled the Code's 25 Ohm requirement?
It does not have to, once you install the second rod the 25 ohm requirement disappears.
weressl said:How will anyone KNOW without testing, if the second rod installation fulfilled the Code's 25 Ohm requirement?
I agree. I would also say that this is one of the sillier aspects of the code. I cannot defend it myself, on technical grounds.iwire said:. . . once you install the second rod the 25 ohm requirement disappears.
charlie b said:I cannot defend it myself, on technical grounds.
charlie b said:I agree. I would also say that this is one of the sillier aspects of the code. I cannot defend it myself, on technical grounds.
weressl said:...and that is why the Code's failure is bordering on criminal.
I don't see this either. Requiring a second rod, without proving it is worth the effort, cannot possibly make the installation less safe.weressl said:...and that is why the Code's failure is bordering on criminal.
It's not a bad idea. But if I were to test the ground rod for the service at my house on a Seattle Summer Day (translation: hot, and has been dry for weeks), and test again on a Seattle Autumn Day (translation: cool, and has been raining for weeks), I will get very different results. So I would stop the code change recommendation at the part at which it says to install two, and quit there.bkludecke said:If I were to propose a code change, it may look something like this:
charlie b said:I don't see this either. Requiring a second rod, without proving it is worth the effort, cannot possibly make the installation less safe.
A single rod, even if the resistance is 5 ohms, without proof, is definitely non-compliant.charlie b said:If a single rod has a resistance under 25 ohms, it is code compliant. If a single rod has a resistance over 25 ohms, it is not code compliant. If I do not measure the resistance of a single rod, then I do not know whether the installation is code compliant or not. To simply say that it is not compliant is saying more than can be known.
But, if you cannot show 10' continuous feet in contact with earth, you must have two rods.iwire said:If you only have a metal water pipe as the electrode for a service you are required to back that up with at least one other electrode of your choice.
LarryFine said:But, if you cannot show 10' continuous feet in contact with earth, you must have two rods.
Sadly, I must disagree with this. Compliance requires either one rod with a below-25-ohm resistance or two rods.weressl said:I think it remains the AHJ's responsibility to show that it is not in compliance.
LarryFine said:If an inspector can't find two rods (or even one for that matter), you can't say "Prove I haven't installed them."
Because, that's why.infinity said:Why not one rod with less than 25 ohms?
It is no such thing! It may be compliant, and it may not be compliant, and you do not know which of these it is. The words in the NEC, as written, do not support your statement.LarryFine said:A single rod, even if the resistance is 5 ohms, without proof, is definitely non-compliant.
LarryFine said:Because, that's why.Okay, not a good answer. :roll:
Because I can buy a whole bunch of rods than I can buy a ground meter for.