So here's the situation -- Data Center, with a 13.8kV service feeds a main-tie-main 480V switchgear (open tie). Transformer size on both ends is 2500kVA Delta/Wye. There is ground fault detection on the 13.8kV service disconnect, but alarm only (LSIA) on the 4000A, 480V mains.
If I look at the language in 230.95 and 240.13 (NEC 2014), it clearly states that only service disconnects 1000A or more are required to have ground fault detection, and based on the design described above, it should be a Code-compliant installation, since the service disconnect is on the 13.8kV side.
But why is this the case? Aren't these 4000A mains just as susceptible to a slow-burn ground fault that would never automatically trip?
It's also been awhile since I was in the data center design industry and can't remember if this is a common practice or not.
Potential fire hazard or just paranoia?
If I look at the language in 230.95 and 240.13 (NEC 2014), it clearly states that only service disconnects 1000A or more are required to have ground fault detection, and based on the design described above, it should be a Code-compliant installation, since the service disconnect is on the 13.8kV side.
But why is this the case? Aren't these 4000A mains just as susceptible to a slow-burn ground fault that would never automatically trip?
It's also been awhile since I was in the data center design industry and can't remember if this is a common practice or not.
Potential fire hazard or just paranoia?