synchro
Senior Member
- Location
- Chicago, IL
- Occupation
- EE
For a wye-delta transformer in a customer facility, it is normally appropriate to avoid connecting a neutral to the center point of the wye primary.
I believe tertiary delta windings are typically rated for a fraction (for example, 1/3) of the kVA rating of the primary and secondary windings. I think this is analogous to having a reduced size neutral, because the current in a tertiary is also related to the amount of load current imbalance. And so I think there is even a stronger case than with a wye-delta to avoid connecting a neutral to the center point of the wye primary.
I believe tertiary delta windings are typically rated for a fraction (for example, 1/3) of the kVA rating of the primary and secondary windings. I think this is analogous to having a reduced size neutral, because the current in a tertiary is also related to the amount of load current imbalance. And so I think there is even a stronger case than with a wye-delta to avoid connecting a neutral to the center point of the wye primary.