We keep our transmission and distribution breakers maintenanced and tested and don't allow the stickiness you evidently are seeing.
This is good, but its difficult to do with tens of thousands of breakers every few years. Especially when for some you need to schedule an outage (straight bus).
Depends on reach. You would normally want your relay to look further and catch those bolted faults. I wil normally set the instantaneous to see 80% of the main line. I will stop at a recloser if it is catching the remainder.
With multiple reclosers in series it gets complicated, ie recloser loops. Parts of the line loose instantaneous clearing.
Sounds like it is time to tweak the budget.
I'd agree, but most EEs aren't the bean counters.
We use alternate (faster and no reclosing) settings when working on the line. It may cause a lockout for what would normally be a blink but so be it.
Yup- work ALWAYS gets a hot line tag.
We assume our breakers will operate during a fault the same way as they did during testing.
Never, ever assume this. Its asking for a blackouts or injury. Thats why despite everything the relaying is duplicated as well as the DC system and communications. Everything besides a casual SCADA trip gets BF relaying initiated. Over reaching zone 2/3, over lapping 50/51, transformer neutral over current, ect as a last resort. MHO reaching through some transformers or even a dedicated 311C for a transformer. Over seas Substations without dedicated busbar protection typically have not just zone 2 from the first supply substation in the chain but zone 3 from the stations before that despite each breaker having a revere zone for BB protection.
Granted every POCO has their own philosophy- but for me and to a lesser degree NERC assume a breaker will fail when called to trip.
But I'm being lazy and want a spoon-fed summary.
If the MV neutral is capable of significant voltages (to remote earth) during any fault condition its isolated from the LV neutral. The LV neutral is then grounded at least 8 feet away where the sphere of influence from the MV rod does not reach the LV ground rod.
Your number of 2.4kv will require that in certain parts of the system the customer neutral must be disconnected and permanently isolated from the MGN.
:happyyes:
I like what Cali does. Though so I've heard that on 3 wire systems they do not ground the can
OK. Haven't ran across it yet.
You will soon enough if you haven't already without knowing. :thumbsup:
It doesn't and I have not said it did.
And thats what I'm getting at. I can legally set my relaying so that a line to neutral fault takes say 60 cycles to clear. 60 cycles of 2.4kv is going to harm someone. Even 5 cycles has risk.
I encourage you to run the numbers on an adult person assuming a resistance from hand to two feet and then compare to the IEC graph.