An SPS2 breaker on its best day clears in 3 cycles page 15:
would you believe a breaker rated to open in 3 cycles will open in 3 cycles or less? I know because we routinely test them.
A breaker that hasn't opened in a while can take a few extra cycles.
Then it is malfunctioning and needs repair.
We don't want to depend on broken equipment in our prtection scheme. That is why we perform routine testing and maintenance.
It takes about 1/2 1 cycle for a microprocessor relay to make a trip decision.
yes
Of course that is best case scenario tripping on definite time or zone 1 MHO (none delayed).
and for your scenario of a phase dropping into a neutral, that is what we expect to happen. In fact, that is what I am most likely to see when reviewing the fault data.
Come real world you have oil breakers that just start at 8-10 cycles.
come real world most that I see are rated faster than that and operate within specs. If you are having breakers operate outside specs then you need to re-work your maintenance schedules and procedures.
Breaker failure that can take 35 cycle to complete.
Backup schemes. We use them as a safety net but also recognize the probabilities are very low that we will have to use them (maintenance and testing, remember?).
You can have an entire station in fault for a very long time. Minutes.
We had that after a contractor melted a lockout relay during testing and did not reveal their mistake. We found out later when a fault occurred and just sat there cooking everything. The DO called and said "hey, your station has some extremely high currents, would you like us to trip it?" It was dragging down the transmission network. Those are the odd scenarios where equipment and people fail but not our planned protection scheme that we consider to be working as it should.
very dependable when maintained.
Inverse time over current tripping if coordinating with a string of other devices.
not our scenario. A bolted L-N fault assumes no fault impedance so we should be hitting 50G and it will win the race (tie at worst) against the 51 relays .
All these add time, 5 cycles is best case in a new system, often a pie dream in old ones.
Quite frankly, you don't know what you are talking about. I work on systems that have been around for 80-100 years and with proper maintenance and testing they don't slow down with age. Where do you get this nonsense?
We tested breakers a few weeks ago that are 60+ years old and 3-cycle rated. The mechanism operated in about 2.5 cycles and the instantaneous relays in about 1/2 cycle.
read the fine print:
"The fault-clearing times designated above are based on broad-application worst-case relay and/or breaker-failure situations. If other fault-clearing times are substantiated, maximum current single cable ratings may be adjusted by calculation on a case-by-case basis."
Peterson coils are used in distribution systems.
But not in a MGN distribution system.
As are remote LV grounds to prevent MV neutral voltage from entering the building.
Please clarify
iwth wye primary distribution transformers, of course!
Kinda need a wye distribution system to go along with your neutral scenario don't you think?
Its not a speculation when it clearly violates IEC 60479-1:
Not my area of expertise as I don't work under that code.