I went to a health care facility last Saturday to do a ground impedance test with an Amprobe INSP-3, so we randomly checked 30 or so outlets. With this meter the highest impedance was about 9.8, some of the low impedance were around 1.3. So I started trying to improve this by removing the grounding electrode from the building steel, wire brushing the building steel and the conductors, also removed the conductor from the cold water pipe and the ground rod and repeated the process. Checked again with the meter and the highest was still 9.8. This plug was out of an IG panel, so I removed the cover and connected a piece of #12 to the isolated ground bar, then ran the other end approximately 175 feet to that outlet. I removed the outlet from the wall, removed the green/yellow wire from the plug and installed the wire that I had laid out on the floor to the outlet and nothing changed the reading was still the same. I removed the wire from the isolated ground bar and installed a receptacle at the panel, I connected the green wire to the receptacle at the panel, and brought the other end to where the cold water pipe was at, disconnected the wire going to the building steel and connected my #12 to the cold water pipe. The results did not change. I reconnected the wire to the cold water pipe along with my #12 and that did not change the outcome either. I removed my #12 from the cold water pipe and took it to the electrical room. I installed it under the acorn clamp along with the conductor that ran over to the panel. Nothing changed. I then disconnected the wire going to the ground rod and connected the #12 to the ground rod only. It read .73 They want the impedance to be 0.2 ohms for systems containing isolated ground receptacles and 0.1 for all others. Any help or information would be greatly appreciated. The service was 800 amps at 480 volts.