Hello, I have a system with a 115kV/12.47kV delta wye transformer where the secondary side of the transformer is grounded with a 200A grounding resistor.
I need to set the 50G/51G secondary main protection (i.e. the main breaker which is fed by the secondary of the transformer and goes on to feed a main switchgear). The CT ratio for the secondary protection 3000:5 and it utilizes residual ground protection (i.e. the relay takes the sum of the three phases to calculate the phase imbalance rather than from a neutral CT or core balance CT). If there is a 200A grounding resistor, this means that the max ground fault on the system is 200A correct?
Don't I want the instantaneous of the relay to pickup at 200 * 5/3000 = 0.33, and then the long time pickup of the relay to pick up at some value much less than that? However, this isn't possible because the relay is just not that sensitive with the given CT ratio. Or perhaps my understanding of resistance grounded systems is wrong. The system was not designed by me, I'm just performing the protection settings of an existing design.
Your help will be appreciated!
I need to set the 50G/51G secondary main protection (i.e. the main breaker which is fed by the secondary of the transformer and goes on to feed a main switchgear). The CT ratio for the secondary protection 3000:5 and it utilizes residual ground protection (i.e. the relay takes the sum of the three phases to calculate the phase imbalance rather than from a neutral CT or core balance CT). If there is a 200A grounding resistor, this means that the max ground fault on the system is 200A correct?
Don't I want the instantaneous of the relay to pickup at 200 * 5/3000 = 0.33, and then the long time pickup of the relay to pick up at some value much less than that? However, this isn't possible because the relay is just not that sensitive with the given CT ratio. Or perhaps my understanding of resistance grounded systems is wrong. The system was not designed by me, I'm just performing the protection settings of an existing design.