Our company is building a 20 foot refrigeration container that will have an on board generator, shore power connections, and the ability to run off of diesel power system, during transport. I have recommended that each system should be shipped with a ground rod, due to the fact that many units may be set up on the ground, running off of shore power, or the on board generator. I have received a fair amount of arguments against including a ground rod. My reasoning would include 250.32 and the following:
A major purpose of “grounding” is toprovide a path so a “short” will trip a breaker. That requires a low resistancepath back to the power source, which is the utility transformer. The pathrelies on a neutral-ground connection required at all [not entirely true]services.
The second "grounding"function is actually a collection of three safety functions:
The 2nd grounding function describedabove is accomplished by connecting the power neutral (the neutral wireentering from the utility company's service) at the service to an earthingelectrode (ground rod).
Does anyone have any additional thoughts for or against?
A major purpose of “grounding” is toprovide a path so a “short” will trip a breaker. That requires a low resistancepath back to the power source, which is the utility transformer. The pathrelies on a neutral-ground connection required at all [not entirely true]services.
The second "grounding"function is actually a collection of three safety functions:
- minimize the voltage between exposed metal and the earth
- minimize the voltage between the power wires and the earth
- provide a sink for lightning, power line crosses, and similar hazards
The 2nd grounding function describedabove is accomplished by connecting the power neutral (the neutral wireentering from the utility company's service) at the service to an earthingelectrode (ground rod).
Does anyone have any additional thoughts for or against?