David Rogers
- Lake County, California
While groud testing a gravel plant where the soil is high concentration of lava rock, the ground rods will not read a resistance of less than 50 ohms. (25 ohms is max resistance) An extra rod has been driven where the grounding electrode conductor at the main disconnect ties to the two rods that are 6 feet apart.
From the main distribution board, there are other subpanels. The conduit feeding each of the subpanels has a bonding conductor that is terminated in the normal mechanical bonding fashion. The the electrical subpanels are mounted on their own support system. All of the conveyors, crushers, subpanels, generation equipment, & etc. are mechanically bonded via a bonding conductor and ground rod system. There are a total of 5 rods and they are tied together, and to the mechanical equipment. These, also, tie back to the main grounding system.
MSHAW is the jurisdiction for this installation. Our company is required to supply a report verifying that the grounding system meets the requirements of 25 ohms resistance. Does the code section, 250-56, indicate that all that can be done has been done by adding the extra rod? And, when I log that there are 50 ohms of resisitance with the one extra rod installed, the system is considered safe and operational and acceptable with MSHAW?