I'm not sure what you are saying here. The code requires that a piece of bare #4 AWG or larger copper wire 20 feet or more in length or a piece of 1/2 inch rebar 20 or more feet in length encased in not less than 2 inches of concrete on all sides shall be used as the Concrete Encased Electrode. If the reinforcing steel is not 1/2 inch or larger; which would be a violation of all of the model building codes; then you can install a 20 foot long bare 4 AWG or larger copper conductor in its place. Viz.
"250.50 Grounding Electrode System. All grounding electrodes
as described in 250.52(A)(1) through (A)(7) that are
present at each building or structure served shall be bonded
together to form the grounding electrode system. Where none
of these grounding electrodes exist, one or more of the
grounding electrodes specified in 250.52(A)(4) through
(A)(8) shall be installed and used.
Exception: Concrete-encased electrodes of existing buildings or structures
shall not be required to be part of the grounding electrode system where
the steel reinforcing bars or rods are not accessible for use without
disturbing the concrete.
250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(3) Concrete-Encased Electrode. A concrete-encased electrode
shall consist of at least 6.0 m (20 ft) of either (1) or (2):
(1) One or more bare or zinc galvanized or other electrically
conductive coated steel reinforcing bars or rods of not
less than 13 mm (1∕2 in.) in diameter, installed in one
continuous 6.0 m (20 ft) length, or if in multiple pieces
connected together by the usual steel tie wires, exothermic
welding, welding, or other effective means to create a
6.0 m (20 ft) or greater length; or
(2) Bare copper conductor not smaller than 4 AWG
Metallic components shall be encased by at least 50 mm
(2 in.) of concrete and shall be located horizontally within that
portion of a concrete foundation or footing that is in direct
contact with the earth or within vertical foundations or structural
components or members that are in direct contact with
the earth. If multiple concrete-encased electrodes are present
at a building or structure, it shall be permissible to bond only
one into the grounding electrode system."
Tom Horne