ground rods @ site poles

Status
Not open for further replies.

jflynn

Senior Member
Maybe this has already been addressed,correct me if I/am wrong but it is not an NEC requirement to install a grd rod @ a site lighting pole.I ask this because a G.C. is telling me he has never seen site poles done without grd rods @ the poles.I told him this is required when designed or shown as a detail, not an NEC requirement...
 
jflynn said:
Maybe this has already been addressed,correct me if I/am wrong but it is not an NEC requirement to install a grd rod @ a site lighting pole.I ask this because a G.C. is telling me he has never seen site poles done without grd rods @ the poles.I told him this is required when designed or shown as a detail, not an NEC requirement...

I believe one could argue that a light pole is a structure thus it needs to follow art. 250.32. Not everyone agrees with this interpretation.

Some say a Pole is a structure-- hard to argue that.
 
Dennis Alwon said:
I believe one could argue that a light pole is a structure thus it needs to follow art. 250.32. Not everyone agrees with this interpretation.

Some say a Pole is a structure-- hard to argue that.
I have a bell box on a stake in my yard. Would that requi....

Oh forget it.
 
Its the exception that allows not to put one in. More than one branch circuit to the pole will require one.
 
RUWired said:
Its the exception that allows not to put one in. More than one branch circuit to the pole will require one.

You are correct. I didn't have my thinking cap on tight enough.
 
donw said:
... service-rated disconnect.
I was going to disagree, but I think you're right. Fortunately, you're the only one who knows, and I can delete your post to keep it that way. :D :D

Sounds like a proposal's in order.
 