Ground rods

Status
Not open for further replies.

Rlmwireman

Member
Location
Evart, MI
Occupation
Electrician
I have a 400 amp and a 200 anp separate
Meters w disconnects on same building. Can I use same 2 grounds
Or do need separate ground rods for each service. As I will tie building steel and cold water to each as well.
Thanks
 
You can and are required to use the same electrodes for all sources on the same building. It's not clear that you actually have two services, if there is only one connection to the utility it is one service. And, if the utility allows, you could put your connection to all the ground rods, steel, water etc. at a single point ahead of the disconnects.
 
You can and are required to use the same electrodes for all sources on the same building. It's not clear that you actually have two services, if there is only one connection to the utility it is one service. And, if the utility allows, you could put your connection to all the ground rods, steel, water etc. at a single point ahead of the disconnects.
I have 2 separate feeds from utility w 2 separate meters
 