Life Study of Rod Type Grounding Electrodes
Ground rods can be constructed of uncoated steel if they are equal to or greater than 5/8" in diameter. This diameter requirement allows for mechanical rigidity for installation as well as mass to allow for deterioration by corrosive action; a ground rod that starts out at 5/8" will take more time to corrode away than one that started out at ?".
It is a very common misconception that the copper electroplating on a rod is used to increase the conductivity. It is not. The resistance of the earth compared to that of the rod itself makes the improved conductivity of the copper plating insignificant. Copper electroplated rods utilize the corrosion prevention characteristics of copper to extend the life of the electrode by as much as 30 years in most soils. The resistance to corrosion allows the copper electroplated rod to be smaller in diameter than the galvanized or steel equivalent. This is also true of stainless steel rods, but the cost of stainless steel is prohibitive for use in everyday installations. The corrosion resistance characteristics of copper-plated steel were demonstrated clearly in the National Bureau of Standards Circular 579 titled ?Underground Corrosion.? This study examined more than 36,000 specimens testing over 300 varieties of ferrous, nonferrous and protective coating materials in 128 test sites in the United States. The study shows that a typical 10-mil copper plating on steel will provide about 40 years of service life versus 13 years for the typical 3.9-mil coating of zinc on a galvanized rod. The results of this study were further corroborated by the ongoing National Electrical Grounding Research Project test of ground rod performance, originally initiated by the Southern Nevada Chapter of IAEI. The results were definitive: The typical copper electroplated rod was virtually free of corrosion while most galvanized rods showed severe deterioration and corrosion after 11 years of service.
mikehughes8 said:Geez
I think they just need to start using gold for ground rods. They are affordable, non-corrosive, and they are better conductors :smile:
stickboy1375 said:The earths resistance is so high anyway...
do ground rods actually prevent any damage from lightning anyway? Is there actually any scientific proof?
Or are we just wasting our time driving these things???
ground rods are very ineffective NFPA 780 compliant LPS.
Let's suppose you have an existing building, no slab (or access), completely gutted, getting a new electric service, and a completely non-metallic water system.stickboy1375 said:So why is the NEC so hardcore about bonding anything to the earth?