I have never seen a GEC buried to a depth of 2'. Is this not required for the GEC esp. when it goes to the second ground rod?
also, I agree the EGC does not have to be continuous to the second ground rod but why by another ground clamp. It's easier to leave it continuous.
There is no depth regiment for GECs
Sometimes it is easer to leave it continuous, sometimes not. :)
There have been many proposals to get a burial requirement for GECs, they have all been rejected for lack of substantiation. 300.5 does not govern the installation of GECs.
300.5 (A) Minimum Cover Requirements Direct-buried cable or conduit or other raceways shall be installed to meet the minimum cover requirements of Table 300.5.
A GEC would not meet the definition of cable here, it would only be a lowly conductor.
Roger
Thanks George & Bob. I always wondered about it and assumed it wasn't a problem, esp. since I have never been hit on it.
Actually, I just reviewed, and a proposal was accepted in the 2005 cycle for a burial requirement. The panel recieved a few comments about the lack of substantiation in the proposal, and it became rejected in the comment phase.
Roger
Since you brought it up... Col. 1 in Table 300.5 says direct burial cables or conductors. Since copper can be buried I would assume that it would be covered there.
Obviously art. 300.5(A) is not quite accurate when it excluded conductors
Agreed.
Or included them
Roger
thanks
thanks
thank you for the illustration and reply. i was at Menards today and they had 8ft long - 1/2in and 5/8 in copper ground rods. any preference or should i look elsewhere? not much price difference between them. thanks Randy