Can you tell me why I would be better off with a ground rod than none?
Reduction, however slight, in step potential near exterior equipment, such as main disco's.stickboy1375 said:Can you tell me why I would be better off with a ground rod than none?
I dont think so... Ground rods are useless IMO...
stickboy1375 said:
I dont think so... Ground rods are useless IMO...
stickboy1375 said:The earths resistance is so high anyway, do ground rods actually prevent any damage from lightning anyway? Is there actually any scientific proof? Or are we just wasting our time driving these things???
brian john said:Then quit driving them and when ANYTHING happens related to the rod or not, be prepared to face the lawyers.
Or Change the code and DEMAND that installers install and test EFFECTIVE ground electrode systems?
RayS said:Well, I think they do help the poco stabilize their system voltages, (by providing a very large, distributed array, across all those xfmrs) and the cynic in me thinks that is why they are required, and why they always will be...
Theoretically, without a ground reference, separate system voltages could float between zero and the sum of max. line voltage between each other.
JohnJ0906 said:What does this picture have to do with grounding a service?
Yes I agree 100%. Much fussing with ground rods, when with a CEE you don't need.brian john said:I do believe at lot of time and energy goes into the rods, when the time and effort could be placed on other elcetrical issues.
LarryFine said:Reduction, however slight, in step potential near exterior equipment, such as main disco's.
/QUOTE]
Sorry but even at 25 ohms it will make not enough difference in the step potential to save your life, unless you stand on the rod, the voltage drops off so fast there is about 90 volts at 3 feet.
Mike H has a great graphic on this but I don't have time to post
A ground rod attempts to extend the equipotential zone outside the bonded area, to try and prevent voltage gradients occurring across the soil, to the benefit of bare footers, cats, and worms. It's not always successful; lose the POCO neutral and that ground rod is dangerous, as is the soil around it.stickboy1375 said:but what i'm looking for is truthful information on what a ground rod can actually do, besides waste my time installing it...
stickboy1375 said:why? they drive their own ground rods...
randypape said:ok guy's all this talk about ground rod's is very interesting. i want to replace my existing ground rods that are in my basement under the service panel. i remodeled and want to cut them off flush with the floor and put a closet in that area and i'll frame around the panel. I was told i could do this but i would have to put in 2 ground rods outside ,8ft into the ground,6ft apart and run a continuous #6 wire into the panel. i was also told these rods needed to be 6ft from the foundation away from the house? where does it say this in the NEC? i sure don't want them sticking that far out into my yard. thanks for any replies Randy
randypape said:i was also told these rods needed to be 6ft from the foundation away from the house? where does it say this in the NEC? i sure don't want them sticking that far out into my yard. thanks for any replies Randy