al hildenbrand
- Minnesota
- Electrical Contractor, Electrical Consultant, Electrical Engineer
A ground screw is not a terminal.
"Terminal" is a somewhat vague, and broad, term, IMO.In my opinion the terminal is the device that connectes directly to the conductor. While screws can be terminals, the screws of a wiring device, I don't see this screw as a terminal, but if you were using it with solid wire it would become a terminal. Screws or bolts are often used to connect a terminal to a bus or other device, but those screws or bolts are not terminals.
The Authoritative Dictionary of IEEE Standards Terms has:
There are a total of ten different meanings from data terminals to semiconductors to substations. Very diverse.terminal (3) (terminal connector) A connector for attaching a conductor to electrical apparatus.
When I join two conductors together, say, an insulated cable to a bus bar, I would consider the lug a "terminal". Most bus bar is in something readily thought of as apparatus. However, if the bus is inside busway, the distinction becomes less clear, IMO.
When I join two conductors together, say two insulated cables joined with a split bolt, I would consider the split bolt a "splice" or a "pressure connector", but not a "terminal".
When it comes to a 10/32 ground screw threaded into the wall of a 4" square steel junction box, one is usually connecting a wire EG conductor to the raceway system EGC. So one is connecting an EG conductor to another EG conductor, however, the junction box can be understood as apparatus, as the box is a part of a raceway system, while also being an EGC.
Apparatus is another nebulous term that has been a source of much opinion and debate on this Forum.
IMO, two ring terminals, as Ishium describes, under one 10/32 ground screw in the wall of a junction box, are not a Code problem.