310.10(H)(2) Conductor Characteristics. The paralleled conductors
in each phase, polarity, neutral, grounded circuit conductor,
equipment grounding conductor, or equipment bonding
jumper shall comply with all of the following:
(1) Be the same length
(2) Consist of the same conductor material
(3) Be the same size in circular mil area
(4) Have the same insulation type
(5) Be terminated in the same manner
Aren't they paralleled in the box? Yes!
First attempt at drawing.
I don't see any parallel conductors (electrically joined at both ends) in your picture, nor have I ever put one in a residence.
If you think that your drawing indicates the presence of an NEC defined parallel conductor, we obviously were taught differently.