I have struggled with this before, and I am still uncertain. But then, with article 250, I am probably not alone in my confusion.
Utility-owned transformer is outside on a pad. Ten conduits will bring the service conductors into the main switchboard. I?ll bond the N&G in the main switchboard, and run a GEC to the ground rods. That part I get. But do I include any ground-thingy (EGC perhaps? or GEC?) or bond-thingy (supply side equipment bonding jumper, perhaps?) in any or all of the 10 conduits? If so, what is it (are they) called, and how is it (are they) sized?
The design drawings (that I am reviewing) presently show 10 conduits, each with 5 conductors (500 MCM AL - 3000 amp service), with the conductors described as A, B, C, N, G. This caught my eye because whatever else might be true, the G wire need not be 500 MCM. My belief is that the G wire is not needed at all, let alone in each of the 10 conduits.
Utility-owned transformer is outside on a pad. Ten conduits will bring the service conductors into the main switchboard. I?ll bond the N&G in the main switchboard, and run a GEC to the ground rods. That part I get. But do I include any ground-thingy (EGC perhaps? or GEC?) or bond-thingy (supply side equipment bonding jumper, perhaps?) in any or all of the 10 conduits? If so, what is it (are they) called, and how is it (are they) sized?
The design drawings (that I am reviewing) presently show 10 conduits, each with 5 conductors (500 MCM AL - 3000 amp service), with the conductors described as A, B, C, N, G. This caught my eye because whatever else might be true, the G wire need not be 500 MCM. My belief is that the G wire is not needed at all, let alone in each of the 10 conduits.