What are you working on up there on the roof?
:slaphead:Hint: This thread is in the solar forum.
PV systems. Had a quality assurance guy write it up saying it can't be on the roof and should be protected in a raceway.
Sent from my SM-G930V using Tapatalk
So for QA purposes it should be in a conduit?See 690.43 (F) if this is an EGC. If it's a 690.47(D) GEC then it's probably code compliant (although if I was the QA guy I'd probably ask you to remove it, but that's a whole other subject... :roll: ).
Just keep in mind that if a ferrous conduit is used the GEC must be bonded to the conduit at both ends to eliminate the choke effect.So for QA purposes it should be in a conduit?
Sent from my SM-G930V using Tapatalk
The relevant code section says that an egc needs to be 6awg if it's not in a raceway. So the QA's argument doesn't hold water from a code standpoint. That said, it doesn't sound like a good practice to me and there might be another code argument against it. Also if this the QA guy not the inspector then there may be a quality standard he's enforcing that exceeds code. My personal quality standard would probably not allow it.
This wouldn't fly on one of my projects, but I agree the Code justification isn't self-evident. When in doubt, inspectors can just flag something that isn't installed in a "neat and workmanlike manner" [110.12].
My first question was: How is that copper secured?
You wouldn't want it screwed down to the roof, as that just creates an opportunity for water ingress. You really wouldn't want it sitting on the roof, as that creates a debris damn. It's hard to say for sure without seeing it, but it sounds dubious (as in there is probably a better way to get from Point A to Point B.)
This wouldn't fly on one of my projects, but I agree the Code justification isn't self-evident. When in doubt, inspectors can just flag something that isn't installed in a "neat and workmanlike manner" [110.12].
I don't know about art. 690 but in 250 #6 is as small as you can go for a grounding electrode conductor without protection.
Ground wire on roof sounds like a contradiction..................
Put it down to me being a Brit.Yes, well, that's not merely a joke.
Maybe they can but they should not.
No NEC inspector should be failing things just because they do not like it. If you can't find a code section directly on point then it is not a true safety issue.
Now on the otherhand customers can certainly have specifications that go well beyond the NEC.