Ground

Bryan-79

Member
Location
Nampa idaho
Occupation
Electrician
I've always use ridged pipe for a ground but an inspector told me I have to pull a ground wire. It says in the code book the ridged pipe can be used as a ground. Any help would be appreciated, thanks.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
As felon says, show the inspector 250.118.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I've always use ridged pipe for a ground but an inspector told me I have to pull a ground wire. It says in the code book the ridged pipe can be used as a ground. Any help would be appreciated, thanks.
That's correct, many metallic raceways (including RMC) are listed as an EGC so no wire type EGC is required. EF gave you the code reference.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
(Note there are a few cases where a wire type grounding conductors are required such as in Art 517)
Can you give more specifics as to the requirement.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Yeah, I guess we need to know the application.
 