Is a step in the same direction as creating an equipotential grounding system around the pool. Steel encased in concrete in general will still have lesser resistance to earth than a rod that has less contact with the earth.This makes sense. I’m going to study it again and knowing this will help.
If you were to place many ground rods in succession and maybe create some sort of bonding of the entire earth from the rod at the house all the way to the rod at the transformer, then you couldn’t get a difference in potential between a hot conductor shorted to the ground rod and ground surrounding it, right? Would that be comparable to equipotential bonding by eliminating touch potential of the ground rod?
You still have potential between this and the "hot conductor" and it is most if not all the potential that the system normally sees between that particular ungrounded conductor and the grounded conductor of the system.then you couldn’t get a difference in potential between a hot conductor shorted to the ground rod and ground surrounding it, right?
What you are doing is keeping the area near those rods closer to whatever potential the grounded conductor is at the point you connected to it.
If there is no current on the ungrounded conductor then that potential is very near earth potential. If there is current on the grounded conductor then there is a voltage drop on the ungrounded conductor, which will make the voltage to earth equal to the amount of voltage that has dropped across the grounded conductor, presuming it is also has a ground reference at the source.