And everything is energized
From transformer N-G GEC to main panel. From main panel to main busbar, from main bus bar to the ground rod.
Because you are making measurements with the system energized, I suggest that you put a clamp meter around the various conductors for grounding that you've mentioned. It's possible that there is current passing through one or more of those conductors... for example, because of more than one bonding point made to the neutral. Such currents could produce small voltage drops across the conductors and that may interfere with resistance measurements and produce incorrect results.