If you measure a significant current through a ground conductor with a clamp meter, then that may interfere with a resistance measurement made across the conductor. But if this happens, I suggest measuring the voltage across the conductor and then dividing it by the current measured by the clamp meter to get the resistance via Omm's law. Use the most sensitive setting on the meter. A true RMS clamp meter would be desireable because there could be harmonics present.
I tried to do line diagram. This are the test and results I received.There is always going to be a small current on the grounding conductor that runs between the NG bond and the ground rod. After that you really shouldn't have any.
I have fluke 376. It should be good for true RMS value