to be clear...

I’ve seen many an install where 10 pipes in and 10 pipes out of 4” conduit with 500’s and 1/0 grounds that were spliced that were not bonded to the box at al. Are you saying that these installs were wrong?

In modern times, Yes.


JAP>
 
In modern times, Yes.


JAP>

To take a tail of 1/0 off each splice and bring it to the housing of the box by either a lug or a ground bar will not be easy. And will look terrible. Does anyone have a photo of one they did?
 
To take a tail of 1/0 off each splice and bring it to the housing of the box by either a lug or a ground bar will not be easy. And will look terrible. Does anyone have a photo of one they did?
You would only need one tail . Maybe best to mount some sort of buss bar inside and terminate to that I think that would look alot better

Sent from my SM-G950U using Tapatalk
 
You would only need one tail . Maybe best to mount some sort of buss bar inside and terminate to that I think that would look alot better

Sent from my SM-G950U using Tapatalk
Mounting said bus bar directly to enclosure is sufficient for bonding to the enclosure - painted enclosure would need to have paint removed at contact point.
 
To take a tail of 1/0 off each splice and bring it to the housing of the box by either a lug or a ground bar will not be easy. And will look terrible. Does anyone have a photo of one they did?

No one ever said making something code compliant was easy.
As for as looking terrible, that would all depend on the workmanship of the install , and the caliber of whoever is looking at it.


JAP>
 