dhducati
Member
- Location
- Pennsylvania
HO wants a new chandelier converted to plugin. Most packaged swag kits I've seen include a two-wire cord and plug, no ECG. The chandelier has exposed metal and a bare #18 EGC together with the two-wire lamp cord. (2005) 410.17(A) says that "exposed metal parts shall be grounded or insulated from ground and other conducting surfaces...". 410.20 says that fixtures "with exposed metal parts shall be provided with a means for connecting an ECG" (which it is). I'm thinking that 410.17(A), with the metal parts insulated from wiring is what allows the two-wire swag kits. Am I reading this correctly?
I'd be more comfortable grounding it, but all of the three-conductor cords I've seen are too large to fit down the center pipe. Thanks for any feedback.
I'd be more comfortable grounding it, but all of the three-conductor cords I've seen are too large to fit down the center pipe. Thanks for any feedback.