Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
If no other overcurrent ahead of the trough taps then the GEC would be no different than doing N/G bond at weather head, or meter and sized accordingly. But, remember N/G bond at one location only. The enclosure in illustration would require a seperate EG bar to land the EGC and eliminate the bonding jumper from the neutral bar.