A single conductor is not a raceway or cable so that wouldn't really apply.
That's what it boils down to, the interpretation of "along the surface of the building construction". If I really had to run the GEC in this fashion I would just use a #4 to remove the interpretive issues.
Correct. I was using 334 as an another example to show what running with the structure is.
It can be on the bottom of the joist if it runs parallel with the joist, IMO. I think that is what Texie was saying. There would be an issue running it perpendicular to the joist. I sensed a bit of confusion here so using parallel and perpendicular explains it clearer.
On the bottom is considered subject to damage because it is a nailing surface. Like the 'face' of a stud. If you staple on the side of a joist the GEC still must be (even thought is not stated) installed like NM in 334.
Wait stay with me here.
in (B)
A 6 AWG grounding electrode conductor that is
free from
exposure to physical damage shall be permitted to be run
along the surface of the building construction without .......
What is free? This is were we have to go to 250.2 Definitions.
Nothing there. So we go to 100.
Nothing there. So we go to 90.
90.1 Purpose.
(A) Practical Safeguarding. The purpose of this Code is
the practical safeguarding of persons and property from
hazards arising from the use of electricity.
What is the practical safeguarding that we are trying to give the GEC?
We go to 90.4 Enforcement. OK What decision do we make that is reasonable and meets the intent of the code.
110.36. Not a circuit conductor.
230.50. Nope.
240.30. Nope.
250.64. Yes but we are back were we started. Keep looking.
250.120 Equipment Grounding Conductor Installation. Kinda of similar so lets read it.
(C) Equipment Grounding Conductors Smaller Than 6
AWG. Where
not routed with circuit conductors as permitted
in 250.130(C) and 250.134(B) Exception No. 2, equipment
grounding conductors smaller than 6 AWG shall be
protected from physical damage by an identified raceway or
cable armor unless installed within hollow spaces of the
framing members of buildings or structures and where not
subject to physical damage.
If it was run with the circuit conductors the EGC would be considered not subject to physical damage.
The example that we (I) am turning this installation down on is a residence so it probably uses NM. So I go to 334 to show the EC why I think the way I do.
334.15 Exposed Work. In exposed work, except as provided
in 300.11(A), cable shall be installed as specified in
334.15(A) through (C).
(A) To Follow Surface. Cable shall closely follow the
surface
of the building finish or of
running boards.
(C) In Unfinished Basements and Crawl Spaces. Where
cable is run at
angles with joists in unfinished basements
and crawl spaces, it shall be permissible to secure cables
not smaller than two 6 AWG or three 8 AWG conductors
directly to the lower edges of the joists. Smaller cables
shall be run either through bored holes in joists or on running
boards. Nonmetallic-sheathed cable installed on the
wall of an unfinished basement shall be permitted to be
installed in a listed conduit or tubing or shall be protected
in accordance with 300.4. Conduit or tubing shall be provided
with a suitable insulating bushing or adapter at the
point the cable enters the raceway. The sheath of the
nonmetallic-sheathed cable shall extend through the conduit
or tubing and into the outlet or device box not less than
6 mm (1?4 in.). The cable shall be secured within 300 mm
(12 in.) of the point where the cable enters the conduit or
tubing. Metal conduit, tubing, and metal outlet boxes shall
be connected to an equipment grounding conductor complying
with the provisions of 250.86 and 250.148.
334.17 Through or Parallel to Framing Members. Types
NM, NMC, or NMS cable shall be protected in accordance
with
300.4 where installed through or parallel to framing
members. Grommets used as required in 300.4(B)(1)
shall remain in place and be listed for the purpose of
cable protection.
300.4
(A) Cables and Raceways Through Wood Members.
(1) Bored Holes. In both exposed and concealed locations,
where a cable- or raceway-type wiring method is installed
through bored holes in joists, rafters, or wood members,
holes shall be bored so that the edge of the hole is not less
than 32 mm
(11?4 in.) from the nearest edge of the wood
member. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
screws or nails by a steel plate(s) or bushing(s), at least
1.6 mm (1?16 in.) thick, and of appropriate length and width
installed to cover the area of the wiring.
(D) Cables and Raceways Parallel to Framing Members
and Furring Strips. In both exposed and concealed
locations, where a cable- or raceway-type wiring method is
installed parallel to framing members, such as joists,
rafters, or studs, or is installed parallel to furring strips, the
cable or raceway shall be installed and supported so that the
nearest outside surface of the cable or raceway is not less
than 32 mm
(11?4 in.) from the nearest edge of the framing
member or furring strips where nails or screws are likely to
penetrate. Where this distance cannot be maintained, the
cable or raceway shall be protected from penetration by
nails or screws by a steel plate, sleeve, or equivalent at least
1.6 mm (1?16 in.) thick.
Does this sound fair? Does it show the EC that I didn't say tough luck I'm the boss?