Most Building Officials (AHJ) would disagree with you. You can't nail to the edge of a stud in a garage or the bottom of a truss or floor joist in a garage.
The #6 and #4. Dennis I agree but the code prohibits it.
Yes I can staple (secure) a 4/0 to the bottom of a joist but not a 12-2. Which causes a bigger 'boom'. Code??????
NO wire or conductor can be stapled to the bottom of a joist paralleled to it. It is a nailing surface.
Why can we go through a cold air return (NM) and not parallel to it? Code.
Smaller cables where prone to be damaged more readily when stabled to the bottom of joist (at angles) because the fasting method tended to cut into the cable (stables) and cause a fault in the branch circuit.
Larger cables generally where fastened with different methods and less prone to damage that lead to faults.
The is little chance that a fasting method even if metal stables is used that will damage a grounding electrode conductor even if the conductor is pulled against the stable or fastener.
If you consider that small cables when pulled on where more prone to damage when pulled on or something laid on top of the cable you can see why additional protection was required for the smaller cables
not to be picky but the area was unfinished basements not garages or did I miss something