Mike, the reason that the NEC requires 1 1/4" from the edge is for nail penetration. Of course if it is drilled then when someone puts sheetrock up it is in danger of being hit but when it is nailed along the bottom of the joist it is protected, IMO, and there is no danger of nails since the grounding electrode conductor would have to be moved.
Again I say to you -- if I use a running board perpendicular to the joist then I can run my cables , grounding electrode conductor or whatever to the bottom of the board. Now how is this any different then the grounding electrode conductor running parallel along the bottom of a joist.
I am sorry you keep quoting code but IMO it is mostly your opinion as to what is being written. Unfortunately it isn't that clear and not everyone sees it as you do. Yes, the protected from damage causes more grief for everyone and is open for the inspector to do as they see fit which, as you know, can be looked at differently by other inspectors.
Wow, who new this would be such a big deal. If I follow correctly, I think we are in the same camp. At first I said it was not compliant but then realized we were talking running along the length on the bottom as indicted in post 13. You I think you have stated it well. The running board comments lend even more credence to the argument that it is legal.