FrancisDoody
Senior Member
- Location
- Durham, CT
Does this requirement exist in your area.
Meter socket can not be used as a grounding point. The grounding electrode conductor shall not be run through the meter socket and the grounding electrode conductor connection shall not be made within the meter provision.
That requirement came from the electrical service requirements for the United Illuminating Company of Connecticut. The on-line handbook.
It just seems that the meter socket should be the place to make that connection. Every socket has a lug attached to the grounded bus to make the connection.
If not let me drag the #6 wire through the socket and I will land it on the EGC bus. But it seems to me that is also prohibited to.
Thanks,
Fran
Meter socket can not be used as a grounding point. The grounding electrode conductor shall not be run through the meter socket and the grounding electrode conductor connection shall not be made within the meter provision.
That requirement came from the electrical service requirements for the United Illuminating Company of Connecticut. The on-line handbook.
It just seems that the meter socket should be the place to make that connection. Every socket has a lug attached to the grounded bus to make the connection.
If not let me drag the #6 wire through the socket and I will land it on the EGC bus. But it seems to me that is also prohibited to.
Thanks,
Fran