bobby ocampo
Senior Member
How do we size Grounding Electrode Conductor if the Service Conductor is 2 sets of 1100 MCM? Is 3/0 the maximum Grounding Electrode Conductor in accordance with Table 250.66?:?
I agree 3/0 is the max grounding electrode conductor one is required to use.
You could still run 3/0 to those, you just do not have to. Finding termination fittings could be a little challenging.unless the GE is a CEE, rod, or plate.
How about the requirement of 250.30 (A)(8)(a) and 250.30(A)(8)(b)
(a) Routing and Sizing. This conductor shall be routed with the derived phase conductors and shall not be smaller than the required grounding electrode conductor specified in Table 250.66 but shall not be required to be larger than the largest ungrounded derived phase conductor. In addition for phase conductors larger than 1100 kcmil copper or 1750 kcmil aluminum, the grounded conductor shall not be smaller than 121⁄2 percent of the area of the largest derived phase conductor. The grounded conductor of a 3-phase, 3-wire delta system shall have an ampacity not less than that of the ungrounded conductors.
What is the 12.5% for?
The 12.5% is also used for sizing the system bonding jumper in an SDS when the derived condcutors are over 1100 kcmil. Same would apply to a main bonding jumper in a service.
Does it mean that 3/0 is not the maximum Grounding Electrode Conductor?
The 12.5% is also used for sizing the system bonding jumper in an SDS when the derived condcutors are over 1100 kcmil. Same would apply to a main bonding jumper in a service.
Does it mean that 3/0 is not the maximum Grounding Electrode Conductor?
Does it mean that 3/0 is not the maximum Grounding Electrode Conductor?
No, #3/0 is the maximum GEC required but bonding jumpers for conductors over 1100 kcmil need to be sized using the 12.5% formula.
So you could have a transformer with 5 sets of 500 kcmil derived (secondary) conductors which equals 2500 kcmil (5*500=2500) and your GEC would be a #3/0, the largest size in T250.66. But the system bonding jumper would need to be sized at 12.5% of the 2500 kcmil. (2500*12.5%=312.5 kcmil) That makes your SBJ a minimum of a 350 kcmil.
Sir can you give examples on how to determine the Grounding Electrode Conductor for parallel application?
Yes, see Article 100. Note, you will find System Bonding Jumper under Bonding Jumper, System.Is there a difference between a Grounding Electrode Conductor and System Bonding Jumper?
Actually it does...the last line says over 1100 kcmil copper uses a 3/0 copper GEC.Table 250.66 did not say that 3/0 is the maximum.
No. Read the text above the two left hand columns.Does table 250.66 applies only for single conductor per phase?
Yes, see Article 100. Note, you will find System Bonding Jumper under Bonding Jumper, System.
Actually it does...the last line says over 1100 kcmil copper uses a 3/0 copper GEC.
No. Read the text above the two left hand columns.
While the last line says above 1100 Kcmil is 3/0 it did not say if it is applicable to single conductor only or multiple conductor only. Otherwise there will be no provision for 12.5%?
Please clarify what the 12.5% is for?
Table 250.66 Grounding Electrode Conductor for
Alternating-Current Systems
Size of Largest Ungrounded
Service-Entrance
Conductor or Equivalent
Area for Parallel
Conductorsa (AWG/kcmil)
Notes:
1. Where multiple sets of service-entrance conductors are used as
permitted in 230.40, Exception No. 2, the equivalent size of the larg-
est service-entrance conductor shall be determined by the largest sum
of the areas of the corresponding conductors of each set.
2. Where there are no service-entrance conductors, the grounding
electrode conductor size shall be determined by the equivalent size of
the largest service-entrance conductor required for the load to be
served.
a- This table also applies to the derived conductors of separately de-
rived ac systems.
b- See installation restrictions in 250.64(A).