It does NOT say "it has to be used as an electrode."I think you are misreading the word "if" to mean you have a choice whether or not to use a qualifying underground water pipe as a grounding electrode. You don't.
You're confusing an underground metal water piping system (1) QUALIFYING as an electrode (250.50) .....with (2) USING it as an electrode.
If it qualifies as one, it has to be bonded to the other Grounding Electrodes per 250.50.
This can be accomplished with a bonding jumper sized by 250.102(C)(1) and bonded to a local metal conduit (i.e. at the water heater) which is bonded to the service entrance enclosure and thus the other GEs per 250.104(A)(1)
Using it as an electrode invokes different codes
250.53(D)(1) requires continuity shall not be interrupted by the water meter. Now we have size a wire according to 250.66 and run it to the street side of the water main.
Different.