Is a grounding electrode in water at the end of a boat dock acceptable as a supplemental ground for a subpanel?
Give us more details on "supplemental ground for a subpanel"
Recent editions of NEC require equipment grounding conductor run with the feeder to "subpanels". Grounding electrodes are only required if the feeder ends at a separate structure.
My question is trying to get more details from the OP on what he has period, pretty vague otherwise. Subpanel already in/on same structure that supplies it doesn't need it's own grounding electrode. If it is in/on a separate structure then it is supplied from it very likely needs a grounding electrode. Have no clue if the boat dock is a separate structure or if the panel is even associated with the dock.Didn't the forum just have this discussion? It was pretty much decided that the code definition of "structure" meant anything more than (and including) a post whacked into the ground as a mounting site for a panel. I think a boat dock meets the NEC definition of "structure."
I'm less and less convinced that ground rods actually do anything useful; a buddy just re-did a 200A residential service, and before he connected the wire to the ground rods (driven regulation 6' apart) he threw his ohm meter across them, and got over 250K ohm... in soaking wet soil.
Tossing a ground rod in a lake can't be any worse.
SeneryDriver
Didn't the forum just have this discussion? It was pretty much decided that the code definition of "structure" meant anything more than (and including) a post whacked into the ground as a mounting site for a panel. I think a boat dock meets the NEC definition of "structure."
I'm less and less convinced that ground rods actually do anything useful; a buddy just re-did a 200A residential service, and before he connected the wire to the ground rods (driven regulation 6' apart) he threw his ohm meter across them, and got over 250K ohm... in soaking wet soil.
SeneryDriver
I question your results as 250 Kohms. What do you mean between rods? That's not how it's measured.
Ground resistivity of soil near my location sets near 25 - 30 ohms when wet with one 8' Cu clad rod. Measured with a clamp on ground resistivity meter.