grounding of SDS

Status
Not open for further replies.

jwelectric

Senior Member
Location
North Carolina
Does the grounding electrode system for the SDS pictured below require that the system be bonded to the building electrode system as outlined in the picture?


25030C.jpg
 

Smart $

Esteemed Member
Location
Ohio
IMO, no... but I see how it can be interpreted that way. The deciding factor is whether the building's water or structural electrode is available [see 250.30(A)(4) and Exception No. 1 thereto]. The NEC does not provide criteria for an available determination. It could mean 10' away, or 3 miles over a mountain top (just a bit exaggerated on that last one :p).

I should add that the picture don't show a connection to water or structural electrodes... but that is where the SDS GES requirement starts. Aside from that, there is nothing specifically says the "remote" SDS must share the same GES as the building.
 
Last edited:

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
IMO, no... but I see how it can be interpreted that way. The deciding factor is whether the building's water or structural electrode is available [see 250.30(A)(4) and Exception No. 1 thereto]. The NEC does not provide criteria for an available determination. It could mean 10' away, or 3 miles over a mountain top (just a bit exaggerated on that last one :p).

I should add that the picture don't show a connection to water or structural electrodes... but that is where the SDS GES requirement starts. Aside from that, there is nothing specifically says the "remote" SDS must share the same GES as the building.

250.30 Grounding Separately Derived Alternating-Current Systems. In addition to complying with 250.30(A) for grounded systems, or as provided in 250.30(B) for ungrounded systems, separately derived systems shall comply with 250.20, 250.21, 250.22, and 250.26.


If the source is located outside the building or structure supplied, a system bonding jumper shall be installed at the grounding electrode connection in compliance with 250.30(C).

(C) Outdoor Source. If the source of the separately derived system is located outside the building or structure supplied, a grounding electrode connection shall be made at the source location to one or more grounding electrodes in compliance with 250.50. In addition, the installation shall comply with 250.30(A) for grounded systems or with 250.30(B) for ungrounded systems.

250.50 Grounding Electrode System. All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.

The answer would be yes it does need to be part of the Grounding Electrode System for the building supplied.
 

Smart $

Esteemed Member
Location
Ohio
250.30 Grounding Separately Derived Alternating-Current Systems. In addition to complying with 250.30(A) for grounded systems, or as provided in 250.30(B) for ungrounded systems, separately derived systems shall comply with 250.20, 250.21, 250.22, and 250.26.


If the source is located outside the building or structure supplied, a system bonding jumper shall be installed at the grounding electrode connection in compliance with 250.30(C).

(C) Outdoor Source. If the source of the separately derived system is located outside the building or structure supplied, a grounding electrode connection shall be made at the source location to one or more grounding electrodes in compliance with 250.50. In addition, the installation shall comply with 250.30(A) for grounded systems or with 250.30(B) for ungrounded systems.

250.50 Grounding Electrode System. All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used.

The answer would be yes it does need to be part of the Grounding Electrode System for the building supplied.
But it does not say it has to be the same GES. The way it is worded, it can be a completely separate GES, considering the SDS a separate structure.

Let's look at a service, to make the point. You have an exterior service MDP 100' away from a building it serves. Do you make up a common GES for both the MDP and the building, or do you establish a separate GES at the MDP, and another at the building?

Getting back to SDS's, look at 250.30(A)(4)

(4) Grounding Electrode. The grounding electrode shall
be as near as practicable to, and preferably in the same area
as, the grounding electrode conductor connection to the
system.
The grounding electrode shall be the nearest of one
of the following:

(1) Metal water pipe grounding electrode as specified in
250.52(A)(1)

(2) Structural metal grounding electrode as specified in
250.52(A)(2)

Exception No. 1: Any of the other electrodes identified in

250.52(A) shall be used if the electrodes specified by
250.30(A)(4) are not available.

Exception No. 2 to (1) and (2): If a separately derived

system originates in listed equipment suitable for use as
service equipment, the grounding electrode used for the
service or feeder equipment shall be permitted as the
grounding electrode for the separately derived system.

Informational Note No. 1: See 250.104(D) for bonding
requirements for interior metal water piping in the area
served by separately derived systems.

Informational Note No. 2: See 250.50 and 250.58 for requirements
for bonding all electrodes together if located at
the same building or structure.


What is depicted in the picture may be the intent, but the words don't back it up 100%.
 

jwelectric

Senior Member
Location
North Carolina
To different opinions on this issue.
Does the picture have an effect on either opinion?
Does anyone think that because the picture has them bonded together that this is what must be done?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
How would that be any different than a meter and disco on a pole in a yard feeding the structure. I have never seen anyone run the gec back to the disconnects on the building.
 

jwelectric

Senior Member
Location
North Carolina
Greg and Smart have opposing opinions on the issue. I agree with Smart that the verbiage in 250.30(C) is the deciding factor in this issue including Informational Note No. 2: See 250.50 and 250.58 for requirements for bonding all electrodes together if located at the same building or structure.

The question was presented to me and the picture was what the question was based on, ?in the picture the electrodes are bonded together so is this a requirement that they be done this way as outlined in 250.58??

The person who presented to question to me made the clear statement that this slide was part of the Analysis of changes 2011 as prepared by the IAEI therefore they felt that the bonding of the two electrodes would be required.

I thought that the question was worthy of discussion therefore I posted it here for discussion. Is the picture an illustration of what is required or does the verbiage of the NEC say something different?
 
T

T.M.Haja Sahib

Guest
How would that be any different than a meter and disco on a pole in a yard feeding the structure. I have never seen anyone run the gec back to the disconnects on the building.
What if the SDS is a high voltage source and the service is of low voltage and the ground of each is of low resistance? In such a case it may be desirable to bond them together.
 

jwelectric

Senior Member
Location
North Carolina
So which is it, do we bond the electrodes together as the picture or are they not required to be bonded together as outlined in the verbiage of the code sections mention thus far?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
So which is it, do we bond the electrodes together as the picture or are they not required to be bonded together as outlined in the verbiage of the code sections mention thus far?

Unfortunately, it may an AHJ call.
IMHO, you do not need to bond the two together.
 

brian john

Senior Member
Location
Leesburg, VA
Whether you intentionally bond them or not they are bonded unless the everything in between is PVC, such as the block heater, battery charger or other periphal equipment circuit would ground/bond the SDS (in this case a generator.
 

RUWired

Senior Member
Location
Pa.
IMO, I think the (250.30(C) graphic is inaccurate.
The required grounding electrode connection to the other sources electrode(s)happens only if present at the SDS source (250.50). The connection to the other electrode(s) from the different sources located at the building being served is already accomplished by the requirement in 250.32(B)2(A) and 250.32(B)1

Also the requirement in 250.58 to use the same electrode contradicts the requirement in 250.30(A)4 via 250.35(A) to be near as practicable and preferably in the same area, if the SDS is remote from the building.
 

jwelectric

Senior Member
Location
North Carolina
Well if this picture was made by the IAEI and is not enforceable how about any other picture that might be published?

I agree that pictures and verbiage found in the NEC are two different things and that only the verbiage can be enforced but we still find some that find pictures and try to enforce what they see in the picture. A very good example of this is what has been hashed out and rehashed out in this forum concerning this picture published by the IAEI in their magazine.

bondinghottocold.jpg



Either is nothing more than a picture and totally unenforceable. We must use the verbiage found in the NEC instead of looking at a bunch of pictures and saying this is how things are to be done.
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
Well if this picture was made by the IAEI and is not enforceable how about any other picture that might be published?

I agree that pictures and verbiage found in the NEC are two different things and that only the verbiage can be enforced but we still find some that find pictures and try to enforce what they see in the picture. A very good example of this is what has been hashed out and rehashed out in this forum concerning this picture published by the IAEI in their magazine.

bondinghottocold.jpg



Either is nothing more than a picture and totally unenforceable. We must use the verbiage found in the NEC instead of looking at a bunch of pictures and saying this is how things are to be done.


I still contend that all ground electrodes that are present at the building or structure served shall be bonded together as stated in 250.50 to create the Grounding Electrode System.
 

Smart $

Esteemed Member
Location
Ohio
I still contend that all ground electrodes that are present at the building or structure served shall be bonded together as stated in 250.50 to create the Grounding Electrode System.
I agree with you. Have to... it's Code. :p

However, how does one determine what electrode is or isn't at the building or structure? Is an SDS generator always a separate structure or always at the building? Is a metal water pipe electrode in the building considered at a generator that's 10' away from the building? Is that as near as practicable to, and in the same area, as the generator? If yes, what if the generator is 200' from the building? What if the water pipe enters on the other side of the building 100' away and there is no structural steel electrode? In practice, there are just too many possibilities, while the NEC has no basis of determination for what is or isn't at a building or structure. :happyyes:
 
T

T.M.Haja Sahib

Guest
Sorry, you were misled by the verbiage of the Code.

Here is why.

Suppose there is a ground fault in the building while the SDS is on. Most of the fault current would return to the SDS via EGC/ neutral of the SDS. But some of the fault current would return via service connection GEC, ground and GEC of the SDS. So there would be neutral to ground voltage at service equipment enclosure as well as at the SDS metallic enclosure for the duration of time, the protective device operates to clear the ground fault. This voltage can be hazardous. But this voltage can be made negligible by bonding the ground rods of the two sources as shown in the OP.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
...

Suppose there is a ground fault in the building while the SDS is on. Most of the fault current would return to the SDS via EGC/ neutral of the SDS. But some of the fault current would return via service connection GEC, ground and GEC of the SDS. So there would be neutral to ground voltage at service equipment enclosure as well as at the SDS metallic enclosure for the duration of time, the protective device operates to clear the ground fault. This voltage can be hazardous. But this voltage can be made negligible by bonding the ground rods of the two sources as shown in the OP.
The connection to the grounding electrode at the building would not make a real change in the voltage to earth under fault conditions, except for a very small area very close to the building grounding electrode. Everything else at the building will be energized with a voltage that is equal to the voltage drop of the fault return path between the power source and the main or system bonding jumper. This is true anytime there is a fault, SDS or not. Everything connected to the electrical grounding system will have this elevated voltage until the fault is cleared, but the earth and metallic objects with a path to earth will remain at "earth" potential.
 