gndrod said:3736, There may be two options if the plumber is using plastic or has the Water Heater in the garage. He's probably avoiding the copper cost crunch too. Let the GC run the UFER rebar if it's ok in your AHJ area. A six pack goes a long way. rbj, Seattle
LarryFine said:Because we're not only not required to, we're not allowed to. Everything lands in the main disconnect enclosure.
gndrod said:Wow, that is a coin flip and no way of telling what is in there unless you are Clark Kent. See if the GC can answer that if you can trust him. If water pipe is being direct buried that is your best bet otherwise I'd back the GES up with rods to be NEC compliant. The UFER must be encased 2" around in concrete at the bottom of the footer in hard-pan per 250.52(A)(3). Also check the 6 AWG size min to match the service size you're going with. Ps. Some contractors skimp with 3/8 rebar (instead of the required 1/2" for a 200A UFER bonded with #4 AWG GEC.)
infinity said:If the contractor were to use 3/8" rebar a CEE is not required.
wireman3736 said:Who knows they could have just dropped the wire down in the wall before the pour.
Not unsafe, just not a 250.52-defined grounding electrode. You can pitch stuff down the formers all day and not hurt anybody.petersonra said:And this would be unsafe in what way?
georgestolz said:Not unsafe, just not a 250.52-defined grounding electrode.
You can pitch stuff down the formers all day and not hurt anybody.
gndrod said:Hi Trevor, Ideally a six pack to get the GC to put in the 1/2" Ufer for you will save the cost of buying and pounding 2 ground rods, bonding jumper, one acorn, one junior weaver, and extra length GEC costly copper. I must have milsled you to think you didn't need to bond to an undersized 3/8" rebar Ufer. My intent being keep an eye what is being installed for the project. The electrical trade takes clever backscratching to save bucks and a six pack is a great trade for a free UFER in the footer stubbed up under the Service Main. BTW, using 3/8" or #3 rebar in footers is a UBC or IRC violation for most stemwall installations. This is my opinion and intended to help future money conscious EC's. rbj, Seattle
Easier if scheduling is easy.infinity said:This would easier and cheaper than using 2 ground rods.
georgestolz said:Easier if scheduling is easy.
Cheaper if gas for that first trip is cheap.
If you've got a crew that can wrap a house in a day's roughing, that extra trip may not be cheaper or easier. Just throwing that out there.
That is so simple it's positively brilliant. I wish I had thought of it first! Thanks, Trevor.infinity said:We try to install the temporary service at the same time the footing is ready for the CEE connection to make only one trip.
georgestolz said:My question remains unanswered: what if the service disconnecting means was outside? What problems could arise at connecting the water pipe electrode at a subpanel?
Bearing in mind that this is illegal. I'm not advocating it, just thinking out loud.
The way I read 250.52 (A) (3), the CEE would still be required by virtue of the " or " in between the 1/2" rod requirement and the 20' of bare #4 option. If the building has footings, the ability to install a CEE would be there and I would take the word " present " from 250.50 as the enforceable kicker.infinity said:If the contractor were to use 3/8" rebar a CEE is not required.
m73214 said:The way I read 250.52 (A) (3), the CEE would still be required by virtue of the " or " in between the 1/2" rod requirement and the 20' of bare #4 option. If the building has footings, the ability to install a CEE would be there and I would take the word " present " from 250.50 as the enforceable kicker.