What does that have to do with anything? Are you saying the code does not cover equipment?
Consider 440.61 and 250.114(3) when it comes to existing grounding-type receptacle outlets on a non-bond wire AC wiring method with utilization equipment cord and plug connected by the dwelling occupant?
That is not what I said and that is not what the code says.
In for a penny, in for a pound. A non-bond wire armored cable installed Lighting Outlet was, let us assume, installed to the Code in effect at the time. . . meaning that, by the Code in effect, the Lighting Outlet contains the EGC.
From the Article 100 Definition of Premises Wiring (System) we know that a Luminaire, while mounted and electrically connected to the Lighting Outlet, is not part of the Premises Wiring (System). The Luminaire is Utilization Equipment connected at an Outlet.
A cord and plug connected residential window AC must be connected to the EGC. The air conditioner is Utilization Equipment connected at an Outlet.
See how that works. Your perspective, with respect to using AC cable armor as an effective grounding means, . . . your perspective causes any one who has plugged in Utilization Equipment listed in 250.114(3) to have violated the rules of the Code in effect today.
And, 250.114(3) has been in effect in today's and earlier Codes long before the EGC rule for Luminaires was upgraded to the version in effect today.
Is the Luminaire connection to an EGC special and requiring upgrading of an un-altered existing non-bond wire AC wiring method. Recalling your response in #70:
In this light why stop at the fan outlet if you know the rest of the house is the same?
Because you have only been contracted to deal with the light. The fix will only take care of that one circuit. If they want me to take care of the rest, I can. I would certainly make some recommendations.
If one is in the dwelling and sees grounding-type receptacle outlets then, by your adherence to only the EGCs of today's NEC, you have to see the receptacle outlets as hazards, a term of art generally requiring immediate remedy.
The term "grandfather" is, indeed, not in the Code. That is beside the point. Enforcement of the Code in effect for new construction for new electrical work done on existing occupancies is generally handled through ordinance worded as in 2008 NEC Annex H 80.9. If not in fact the wholesale adoption of the unaltered language of 80.9 as local ordinance. Annex H 80.9(B) and 80.9(C) are the heart of the meaning of the trade slang term "grandfathered".