al hildenbrand
Senior Member
- Location
- Minnesota
- Occupation
- Electrical Contractor, Electrical Consultant, Electrical Engineer
Thank you for the reference to this recent research. It's too bad that it is shrouded by a fee.Some of the findings should make you think twice about accepting unbonded armored cable as an adequate EGC or even safe in its existing condition, grandfathered code or no grandfathered code.
Your synopsis has been instructive. I look forward to learning more.
That said, I turn back to the original post and the situation described. Based on the OP and subsequent clarifications, I understand that residential dwelling to have bond wire AC installed.
A ceiling fan was replaced. Does connecting the new ceiling fan EGC to the AC method EGC make the installation worse?
No.
In your own words, Mivey, you wouldn't loose sleep over the slight weakness of the AC bond wire sheath EGC.
A simple resistance check will determine if the workmanship of the OP dwelling's EGC is still most likely to be intact.
Now, I'm still not sure about how a ceiling fan is "ground hungry", in your term, but having the exposed conductive parts of the fan connected to even the AC EGC is better than not. Especially since the NEC has consistantly told us that both non-bond and bond AC are effective grounding means.