texie
- Fort Collins, Colorado
- Electrician, Contractor, Inspector
Or fuses as I mentioned back in post #5.what if the appliance had a circuit breaker that was only slash rated?
If it's part of the equipment it would not be a concern to an electrician providing power to it.what if the appliance had a circuit breaker that was only slash rated?
If the equipment requires a specific type of system the manufacturer should specify the type circuit.Or fuses as I mentioned back in post #5.
One orange, one white.I'm curious.
What wire color would you choose to pull to the 208v Load?
I would think it would be a concern. I can supply 208 volts to a slash rated breaker with two wires at 120v each being compliant and safe within the specs of the breaker. I can also supply 208v on one leg and 0v on the the other, which would not be compliant and/or safe with a slash rated breaker. If I'm landing my wires on the breaker or fuse holder I feel I should follow code up to that point.If it's part of the equipment it would not be a concern to an electrician providing power to it.
Roger
Once again, what's inside of a listed (or not) piece of machinery is not my concern if there is not some information or warning to tell me to provide something specific as field wiring.I would think it would be a concern. I can supply 208 volts to a slash rated breaker with two wires at 120v each being compliant and safe within the specs of the breaker. I can also supply 208v on one leg and 0v on the the other, which would not be compliant and/or safe with a slash rated breaker. If I'm landing my wires on the breaker or fuse holder I feel I should follow code up to that point.
And I see it the opposite, like the NEC, if it doesn't say I can't do something I can.That's my whole point, without information from the manufacturer I wouldn't blindly state you could supply any 208v circuit and throw any issues back at the appliance maker. I would want to know what the appliance says. It can be a concern.
Sent from my SM-G973U using Tapatalk
I agree I follow the NEC as well. I just re read the OP,s post and noticed where he says it requires 2 wires. After 2 days I forgot that he said 2 wires and I was just thinking it needed 208 V without any other information. I didn't remember reading the two wire statement. My bad.And I see it the opposite, like the NEC, if it doesn't say I can't do something I can.
Roger
Roger
This is feeding a cooking appliance that only requires 2 wires.
Odd, probably is to most. Grounded conductors still required to be white or gray. Corner grounded delta should also have white or gray for the grounded phase conductor.I can say it would be very odd to see a white conductor pulled to a strictly 208v single phase load.
Jap>
Kind of logical, until you realize orange is already one of your 480 volt system colors.One orange, one white.
A buck-boost is slang for an autotransformer arrangement of windings. In an autotransformer there is a conductor which is common to both the HV and the LV sides of the transformer. The output is not a separately derived system
The OP has an isolation transformer which does not have a conductor (other than ground) common to both sides of the transformer. The out is a separately derived system.
That is exactly what I'm saying. If the equipment has specific instructions I would have to follow them, if they do not then I will supply what is available and convenient regardless of the internal components.But if you were hired to supply power to a piece of equipment wouldn't 110.3 (B) and N (C) Listing apply? (NEC 2017)
But every time you have done it before you didn't have a grounded conductor involved, OP's application would be, unless he leaves this secondary ungrounded, but then he really needs to have ground detection installed.I said odd because I've never pulled a white or gray or and grounded conductor color for that matter to a strictly 208v load, nor ever would I.
JAP>