The site lighting at a majority of the Rest Areas and welcome centers in PA have been wired using a multi circuit branch circuit. They were installed using a three wire direct buried cable between the lights. (Two hots and one neutral). NO EQUIPMENT GROUND WAS INSTALLED. They had the neutrals bonded to each pole and each ground rod at each pole. The engineer is arguing with me that this is a legal installation according to 250.32(B)(2). Our company was called to inspect the wiring due to people complaining that they where getting shocked off the poles. "DUH" We eliminated the bond between the neutral conductor and the poles and ground rods and told them that was a temporary fix, and that they had to either install an equipment ground or change the circuit and ballasts to 480volt 1phase and then the neutral could be changed to an equipment ground. Could someone please clarify that what we did and are telling him is correct?