xformer
- Dallas, Tx
- Master Electrician
Is it still Permissible to omit a receptacle bonding jumper under certain conditions?
Can you be a little more specific with the question?
Roger
I am wondering if the bonding jumper to a grounding terminal on the receptacle is required or am I still permitted to omit it in cases of self grounding receptacles.
(B) Contact Devices or Yokes. Contact devices or yokes designed
and listed as self-grounding shall be permitted in conjunction
with the supporting screws to establish the grounding
circuit between the device yoke and flush-type boxes.
Doesnt this violate the Section in 406 requiring the grounding terminal to be connected to the EGC?
here is the handbook