I will make one correction, and leave any more for others.Maybe, maybe not.
I'd like to think that I am doing those things. I follow the rules I've been taught. But it still doesn't mean I understand all of the reasons why.
The quote I replied to said this "the "EGC" is serving more than one purpose - it is fault clearing AND connecting equipment to earth." I don't understand at all the earthing part. As I understood it (until now) the EGC was to carry fault current back to the neutral buss, which is in turn connected to earth via the GEC thru the water service which is connected to earth. The current would flow thru the earth to the wire that runs up the side of the utility pole.
Please correct all that you see fit.
Thanks
Mike
In the case of a fault from hot to some exposed metal connected to the EGC, the fault current will follow the EGC back as far as the main panel where the EGC is bonded to the service neutral and will follow that path back to the X0 terminal of the POCO transformer. Some small portion of that may instead follow the earth-based path you describe.
Only if the POCO neutral is compromised will all of the current be forced to go via the earth either to the POCO ground rod or more likely to the working utility neutral attached at another nearby house on the same water supply or other common ground electrode.