electrofelon
- Cherry Valley NY, Seattle, WA
- Electrician
Ever take a voltage reading? That voltage is in reference to what? EARTH
Because it connects all non-current carrying metal that encloses electrical wires and equipment to earth.
Bonding is something like ensuring electrical continuity around expansion joints in metal conduit, the metal boxes used in non-metallic cables, the jumper installed from a metal box to the metal yoke of devices where metal raceways are used.
And it also provides a low impedance path back to the source. If you are so intent on calling it what it does, shouldnt you be wanting to call it the "equipment grounding and bonding conductor"?
Bonding rules are a lot more lax than equipment grounding so to change the name of equipment grounding to equipment bonding is going to change the rules of the earth connection and the potential of earth and a metal non-current carrying that is elevated above earth. Read 250.4(A)(1) and (2) for more information on the subject. When you read this for a few minutes forget about bonding and let nothing but earth be on your mind. Once this has sunk in real good then proceed with the bonding of your choice.
How do you conclude that bonding rules are more lax than equipment grounding? Actually I would say that this would be a difficult debate to have because 250 is such a mess and splitting it up into two articles, fault clearing and bonding, is more important IMO than changing EGC to EBC. Tell me this: Article 250.24, are they talking about system grounding, equipment grounding, or fault clearing? I say after reading 250.4(A)(1) they must be talking about system grounding. Glad we got that straightened out. Everyone agree? 250.24 is about system grounding only. The whole part VI of article 250, are they talking about system grounding, equipment grounding, or fault clearing paths? Again reading 250.4(A)(1) I conclude they are only talking about equipment grounding (earthing). Everyone agree there?