Al Dagys said:I know the water ground required to ground a 200A residential panel is #4AWG, but what size is required from the meter socket to the panel which must be connected to the grounding bushings? Is it #4 or #6???
No, actually they don't. You can use a plastic nipple. You can also use a bonding locknut on one end if you don't have any knockout rings left.Al Dagys said:They do require grounding bushings and a ground wire.
Al Dagys said:The inspectors by me(just outside Chicago) want this wire to do the following: Connect to the nuetral bar inside, through the grounding bushing inside the panel, through the grounding bushing inside the meter socket, then to the lug on the meter socket itself. This wire must be unbroken. Then a seperate wire from the lug on the meter socket unbroken to the ground rod.
resistance said:That's a lot of work.
I agree 100%! Why are you telling me!?:grin:Dennis Alwon said:That's creating a parallel neutral and that's illegal
resistance said:I agree 100%! Why are you telling me!?:grin:
I'm also on board with MD.
Al Dagys said:Parallel nuetral? Could you please explain what that is? These inspectors out here are insane. We used to have to only use 2" locknuts and a plastic bushing untill these "inspectors" went to some seminar and now they require metal grounding bushings and ground wires between the panel and the meter socket.
Al Dagys said:I do not understand. The nuetral bar is bonded to the panel with a bonding screw(which is required by inspectors). How is this a parallel nuetral? The nuetral and ground are the same at this point. We are required to use all conduit in residential buildings, does this change anything?
Al Dagys said:They do require grounding bushings and a ground wire...I have failed inspections before. The debate is the size of the wire.