Senior Member
.....I would not include a ground enhanced electrode in any studies as we can not use them when installing to the NEC, home owners are not going to maintain them. ....
What section prohibits this ??
.....I would not include a ground enhanced electrode in any studies as we can not use them when installing to the NEC, home owners are not going to maintain them. ....
I'm not trying to correct anyone, just become more knowledgeable. I also would like to thank you for posting the information. It clearly shows there are better grounding methods than what we typically use.
To me the question becomes do we need 'better electrodes'?.....
I appreciate what Gary did, he really worked hard in providing us with his experiment. I am curious how practical it really is.
In regards to your comment about shock hazard, is that the reason behind installing electrodes and the grounding electrode system?[/QUOTE]
It is one the biggest myths that surround the grounding electrode system, and it is why it is so blown out of proportion, because of the mis-understanding of what bonding to Earth can really do.
The problem here is not many understand, the results that we find in Gary's experiment, they lean toward the myth, that a lower resistance of an electrode will open a OCPD, but they miss that not all circuits are low current(15/20amp) and that the earth can not be depended upon to consistency open a breaker.
So this only leaves the other reason of requirement, lowering the voltage to earth, as in touch potential, and we can now see (because of Gary's experiment) that the better the conductivity of Earth, the higher the touch potential.
Now for the NEC requirements for an electrode:
To limit voltages of a higher source?
we know the voltage drop across a given resistance will be the same at a given current, so if I have a 25 ohm rod that will produce a 90 volt potential at 3' from the rod, it will not matter if the source is at 120 volts or 7200 volts, you will still have a touch hazard. will the 7200 volt OCPD open? in most cases it should, but I have posted one such case it didn't, even with 4 rods, and still did a lot of damage to the house and the equipment in it, and if there was any contact of a person to anything grounded in those two houses, they would have been dead, or close to it.
Ground rods do nothing in an NEC building to make a building safe from shock or fire, period!
I appreciate what Gary did, he really worked hard in providing us with his experiment. I am curious how practical it really is.
In regards to your comment about shock hazard, is that the reason behind installing electrodes and the grounding electrode system?[/QUOTE]
It is one the biggest myths that surround the grounding electrode system, and it is why it is so blown out of proportion, because of the mis-understanding of what bonding to Earth can really do.
The problem here is not many understand, the results that we find in Gary's experiment, they lean toward the myth, that a lower resistance of an electrode will open a OCPD, but they miss that not all circuits are low current(15/20amp) and that the earth can not be depended upon to consistency open a breaker.
So this only leaves the other reason of requirement, lowering the voltage to earth, as in touch potential, and we can now see (because of Gary's experiment) that the better the conductivity of Earth, the higher the touch potential.
Now for the NEC requirements for an electrode:
To limit voltages of a higher source?
we know the voltage drop across a given resistance will be the same at a given current, so if I have a 25 ohm rod that will produce a 90 volt potential at 3' from the rod, it will not matter if the source is at 120 volts or 7200 volts, you will still have a touch hazard. will the 7200 volt OCPD open? in most cases it should, but I have posted one such case it didn't, even with 4 rods, and still did a lot of damage to the house and the equipment in it, and if there was any contact of a person to anything grounded in those two houses, they would have been dead, or close to it.
Ground rods do nothing in an NEC building to make a building safe from shock or fire, period!
Wayne
I am not sure, but I do not believe you and I are on a different page, maybe just stating it differently.
I will say that limiting the voltage does not mean eliminating it. There are times the electrode system will help when the higher voltages are introduced to a building, and other times it will not. I am not an expert in explaining or understanding why. I will say I believe it mostly has to do with the resistance introduced due to soil conditions and distance to the utility protection.
we see that basically as the conductivity of Earth increases, the sphere of influence decreases, and this can increase the shock hazard, as higher voltages will be available closer surrounding the electrode, so touch potential, is increased. so instead of 90 volts at the 3 foot mark, you might have 105 volts.
so over all, it would be in my opinion that even having a better electrode, as far as an NEC requirement, would lead to a higher potential of touch and shock hazard, and is probably one of the best reasons to get rid of the requirements for grounding rods, and some of the other electrodes.
Wayne
I am not sure, but I do not believe you and I are on a different page, maybe just stating it differently.
I will say that limiting the voltage does not mean eliminating it. There are times the electrode system will help when the higher voltages are introduced to a building, and other times it will not. I am not an expert in explaining or understanding why. I will say I believe it mostly has to do with the resistance introduced due to soil conditions and distance to the utility protection.
I think were close to being on the same page, just the issue with the voltage limiting factor of a electrode.
Only if the electrode can open the OCPD can it protect a building.
The problem with the thinking that the electrode will limit the voltage on a building, is, that almost all the voltage drop will be across the electrode, not on the conductors from the source.
it the case of the two houses I had encountered, the amount of damage, clearly showed that almost all the 7200 volts was present in the building and electrical system, and the burn marks around the electrode indicated that almost all the voltage drop dropped across the Earth surrounding the electrode. this left the building at close to the full 7200 volts because of the low impedance path it came into the building on (the service neutral)
if we were to place a 120 volt on the building that had no other low impedance reference to the X0 of the source, other than the ground rod, this building will be at 120 volts to Earth, all the voltage will be dropped in a very short distance around the electrode, not evenly across the wiring in a building or the conductors running out to the pole. so because of this, the building will have almost the full potential of the circuit feeding it, as the resistance of the conductors feeding the building are much lower in resistance than the resistance of the electrode.
Its simple math, of two series resistors, one the low resistance of the conductors, and the other the high resistance of the electrode.
So the bottom line is, if the OCPD does not open, the voltage will be present on all the grounding of the building.
I think were close to being on the same page, just the issue with the voltage limiting factor of a electrode.
Only if the electrode can open the OCPD can it protect a building.
The problem with the thinking that the electrode will limit the voltage on a building, is, that almost all the voltage drop will be across the electrode, not on the conductors from the source.
it the case of the two houses I had encountered, the amount of damage, clearly showed that almost all the 7200 volts was present in the building and electrical system, and the burn marks around the electrode indicated that almost all the voltage drop dropped across the Earth surrounding the electrode. this left the building at close to the full 7200 volts because of the low impedance path it came into the building on (the service neutral)
if we were to place a 120 volt on the building that had no other low impedance reference to the X0 of the source, other that the ground rod, this building will be at 120 volts to Earth, all the voltage will be dropped in a very short distance around the electrode, not evenly across the wiring in a building or the conductors running out to the pole. so because of this, the building will have almost the full potential of the circuit feeding it, as the resistance of the conductors feeding the building are much lower in resistance than the resistance of the electrode.
So the bottom line is, if the OCPD does not open, the voltage will be present on all the grounding of the building.[/quote]
Wayne
I do not see this as a grounding issue related to the grounding electrode system (250.4(A)(1)&(2). I see it as a bonding issue (250.4(A)(3)&(5).
Only if the electrode can open the OCPD can it protect a building.
So the bottom line is, if the OCPD does not open, the voltage will be present on all the grounding of the building.[/quote]
Wayne
I do not see this as a grounding issue related to the grounding electrode system (250.4(A)(1)&(2). I see it as a bonding issue (250.4(A)(3)&(5).
Or protect people.
For a wood pole?UFER:roll:
I was just trying to show that most of the required electrodes serve no purpose in the NEC. the science is not there to back their requirement.
was't the op concerned about damage caused by lightning??
Where does Pepsi fall in the ratings?For the most part , Coke is one of the lowest ground enhancement one can find.
Where does Pepsi fall in the ratings?
was't the op concerned about damage caused by lightning??
um errr well yes, But I thought that was summarized pretty well in the first response
Do you know of a way to guarantee protection against a direct lightning strike?
If you do I'm all ears
OK let me see if I understand ,... Lightning protection systems are rabbit crap,.. is that pretty much your opinion?